Thread: Wiring for Compressor

  1. #1
    Marty57's Avatar
    Join Date
    Jan 2005
    Location
    Nipomo, Ca
    Posts
    1,373
    Post Thanks / Like

    Wiring for Compressor

    I bought a new compressor, Ingersoll Rand 60g 5hp single stage.

    IMG_6203.jpg

    Working on hooking it up and wiring it. I would like to plug it into the same circuit I used for previous compressor. I only have one 230V outlet in my shop (4 prong from dryer, moved dryer outlet from house to shop). For existing compressor, Arch Welder and Tig welder; I have a three prong to four prong extension cord with a box on the end and it works fine, I taped off the white wire from the four prong cord inside the box.

    I would like to use a 35-6 dryer cord to wire the compressor; will that work? The control box on the compressor has black, white, and green terminals. Can I hook up the white to white, black to black, and green to green and tape off the red terminal from the 35-6 cord inside the control box for the compressor? Or, should I wire the compressor with the same three prong as the Tig and Arch welders and use the adapter cord I have? Web, you helped me when I made the extension cord and it has worked great, thanks. Now, how to wire the compressor?

    Here's the adapter cord I have been using:

    IMG_6401.JPG

    Here's the cord I would like to connect to the compressor to match the wall outlet:

    35-6 cord.jpg

    And last, here is the control box on the compressor:

    IMG_6216.jpg

    Can I use the new cord with this compressor by just taping off the red wire?

    Thanks,
    Marty

    added one more picture, from the motor:

    IMG_6217.jpg
    Last edited by Marty57; 01-30-2019 at 04:01 PM. Reason: added info
    N367PS
    Psalm 36:7 "High and low among men find refuge in the shadow of His wing"
    www.marty2plus2.com
    Likes KelvinG liked this post

  2. #2
    PerryB's Avatar
    Join Date
    Aug 2007
    Location
    Northern Calif.
    Posts
    1,744
    Post Thanks / Like
    How big is the circuit and what is the compressor rated at, 30A? As long as the compressor doesn't overtax the circuit, no sweat. You don't need the 4th leg. It's just a neutral, which allows you to safely/correctly get 120v out of a 240. All you need for 240 single is the two hots and the ground. It really doesn't matter which route you choose, you're effectively doing the same thing. From a simplicity standpoint, if the comp. already fits the adapter cord I'd just go ahead and use it.
    Last edited by PerryB; 01-30-2019 at 04:09 PM.
    After Monday and Tuesday, even the calendar says WTF !

  3. #3
    Marty57's Avatar
    Join Date
    Jan 2005
    Location
    Nipomo, Ca
    Posts
    1,373
    Post Thanks / Like
    No wiring on new compressor yet, 4 prong cord is easy to get already made up. Circuit is connected to two 30A breakers ganged together. Compressor is rated at 24.4A so I think the circuit should handle it ok. Thanks for the advice.
    Marty
    N367PS
    Psalm 36:7 "High and low among men find refuge in the shadow of His wing"
    www.marty2plus2.com

  4. #4
    Eddie Foy's Avatar
    Join Date
    Dec 2014
    Posts
    3,307
    Post Thanks / Like
    Depends how the ext cord is wired. Standard is red and black for the two hot phases. Green Ground. White neutral which you won't need.

    The motor is wired black and white for the two hots and green ground. No neutral.

    So you would go motor black to cord black. Motor white to cord red. Green to green.
    Last edited by Eddie Foy; 01-30-2019 at 04:40 PM.
    "Put out my hand and touched the face of God!"

  5. #5
    wireweinie's Avatar
    Join Date
    Aug 2013
    Location
    Palmer, AK
    Posts
    2,326
    Post Thanks / Like
    Not sure a dryer cable is big enough. Do you know what gauge it is?

    Your two hot legs are going to be the flat blades on the plug. Ring those out to see what colors they are. Then either one can hook to the black wire on the compressor box and the other to the white wire. You'll have to figure out which of the round blades has continuity all the way back to the wall box. That blade will connect to the green at the compressor box.

    Not complicated but the color codes may be mixed here, so check everything with a volt/ohmmeter.

    Web
    Life's tough . . . wear a cup.
    Likes Eddie Foy, Hardtailjohn liked this post

  6. #6
    Marty57's Avatar
    Join Date
    Jan 2005
    Location
    Nipomo, Ca
    Posts
    1,373
    Post Thanks / Like
    The extension cord I made up has the white taped off. So, I’ll use red on dryer cord to white on motor and black to black, green ground; white on dryer cord not used, sound righ? Size of dryer cord I am looking at is same size as motor to control box on compressor. Size is 8/2 on dryer cord, rated for 50A. Sound right so far?
    Thanks,
    Marty
    N367PS
    Psalm 36:7 "High and low among men find refuge in the shadow of His wing"
    www.marty2plus2.com

  7. #7
    wireweinie's Avatar
    Join Date
    Aug 2013
    Location
    Palmer, AK
    Posts
    2,326
    Post Thanks / Like
    Verify before using a color!

    If the dryer cord is the same gauge as the wire on the compressor you should be good.

    Web
    Life's tough . . . wear a cup.
    Likes PerryB, Hardtailjohn liked this post

  8. #8
    Marty57's Avatar
    Join Date
    Jan 2005
    Location
    Nipomo, Ca
    Posts
    1,373
    Post Thanks / Like
    Quote Originally Posted by wireweinie View Post
    Verify before using a color!

    If the dryer cord is the same gauge as the wire on the compressor you should be good.

    Web
    Same size as on compressor. Thanks
    Marty
    N367PS
    Psalm 36:7 "High and low among men find refuge in the shadow of His wing"
    www.marty2plus2.com

  9. #9
    irishfield's Avatar
    Join Date
    Feb 2003
    Location
    Penetanguishene, Ontario Canada
    Posts
    2,937
    Post Thanks / Like
    Manufacturer should be SHOT for not at least putting Black or better yet Red tape on that white wire if it's indeed wired for 220/240 volts!

    Use the cord, Black to Black.. Red to the compressor White, Green to Green, Tape the cords White off, or better yet cap with a marret.

  10. #10
    cruiser's Avatar
    Join Date
    May 2002
    Location
    South Glens Falls, NY
    Posts
    1,436
    Post Thanks / Like
    No, it will not work as you describe. The flat blades on your cord are the hot blades and are connected to the red and black wires. The white and green wires are connected to the round spades and are your neutral and ground respectively. Check your PM’s and find yourself a qualified electrician

  11. #11

    Join Date
    Dec 2004
    Location
    Inkom, Idaho
    Posts
    1,251
    Post Thanks / Like
    No need for a plug at all, and I'm surprised no one else mentioned that, any qualified Sparky can just hardwire it in, unless you're planning on moving it around? I did my own, same size/HP, right from the shop's main panel, so didn't need to figure out what cord color went in which blade, etc. It was obvious the two hots went to the 240 breaker, and the bare copper went to the ground. Just three wires to disconnect when you wear it out and buy another, your plugs just complicate things it sounds like!

  12. #12
    PerryB's Avatar
    Join Date
    Aug 2007
    Location
    Northern Calif.
    Posts
    1,744
    Post Thanks / Like
    Just use an ohm meter to trace the legs of the cord before you make any connections, that takes the guesswork out of it. The "L" shaped pin SHOULD be the white, and that's the neutral you won't be using. The two flat pins are hot (120v each relative to ground/neut. -- 240v between them) and the round is ground.
    After Monday and Tuesday, even the calendar says WTF !

  13. #13
    Marty57's Avatar
    Join Date
    Jan 2005
    Location
    Nipomo, Ca
    Posts
    1,373
    Post Thanks / Like
    Quote Originally Posted by courierguy View Post
    No need for a plug at all, and I'm surprised no one else mentioned that, any qualified Sparky can just hardwire it in, unless you're planning on moving it around? I did my own, same size/HP, right from the shop's main panel, so didn't need to figure out what cord color went in which blade, etc. It was obvious the two hots went to the 240 breaker, and the bare copper went to the ground. Just three wires to disconnect when you wear it out and buy another, your plugs just complicate things it sounds like!
    Problem with wiring it direct is first, I don't have a panel in the garage/shop; the service panel is on the other end of the house and outside. Second, although I'm not moving it around, I do need to use that outlet when I need to use the Tig or Arch welder. I need to unplug compressor so I can run the Tig on the circuit. With the service to the garage/shop, if I were to put in a sub panel and hardwire the compressor and have an outlet for the Tig or Arch, I would get dinged by code. I don't think I have enough amps or sized cable to run both the compressor and Tig at same time. Even though i don't plan on running both simultaneously, if the set up would allow that to happen the wire needs to be larger. I had that in another shop and had to change it when I moved because it was out of code. I hope I'm being clear.

    I'm trying to avoid spending more than the cost of the compressor to run a dedicated circuit to the shop. Is it against code to have this type of compressor on a cord? Would it be better to change the outlet in the wall to three prong NEMA 60 (matching the Tig and Arch welder)? Can that be done? Maybe eliminating the extra wire at the outlet and back in the service panel? I'm not against bringing in an electrician but I want to have a good idea what's legal rather than someone trying to sell me a $1K rewire that I really don't need.

    So, would I be better off changing the wall outlet to the Nema three prong that is currently on the end of my adapter/extension cord, and have all three devices with the same plug and eliminate the need for the cord/adapter completly? Or, just use a 4 prong plug on the compressor eliminating the extra natural?

    Thanks,
    Marty

    Thanks for the education so far; getting closer to a solution I think.
    N367PS
    Psalm 36:7 "High and low among men find refuge in the shadow of His wing"
    www.marty2plus2.com

  14. #14
    Gordon Misch's Avatar
    Join Date
    Dec 2003
    Location
    Toledo, Wa (KTDO)
    Posts
    3,271
    Post Thanks / Like
    Marty, sent you an email - -
    Gordon

    N4328M KTDO
    My SPOT: tinyurl.com/N4328M (case sensitive)

  15. #15
    wireweinie's Avatar
    Join Date
    Aug 2013
    Location
    Palmer, AK
    Posts
    2,326
    Post Thanks / Like
    All matching plugs would be nice but not necessary. Up to you.

    Web
    Life's tough . . . wear a cup.
    Thanks Marty57 thanked for this post

Similar Threads

  1. Need help wireing up air compressor
    By Marty57 in forum All Things Electrical
    Replies: 40
    Last Post: 04-19-2016, 08:18 PM
  2. Air Compressor?
    By supercub in forum Cafe Supercub
    Replies: 14
    Last Post: 07-19-2009, 01:42 PM
  3. Big compressor
    By Tim in forum Products, Purchases, Reviews & Prices
    Replies: 7
    Last Post: 01-15-2008, 05:33 PM

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •